So I'm still working with a NorCal property owner needing service to an upcoming house & pool.
We'd really like 3ph 208/120 wye; for a welder & a number of pumps: deep well, swimming pool/slides, and fire protection. The rub is, the house is 750 ft back crow-fly from the 3ph-221.5 kv pole line & PG&E wants a 1400 ft long route. PG&E has guesstimated $60k for that, and quoted us only (!!!) $29K for split phase 320A 240/120.
I gather that a large part of the $60K is that 3-ph is considered 'Special Facilities' & such is heavily marked up under Rule 2. [This is part of the muddle; I was told by Engineering that a 7.5+ HP motor would take us out of Special Facilities, but the lower level people disagree.]
However, we recently found out several details they had, well... I'll just say 'overlooked' telling us, and as a result we had a meeting with them. Now it seems we can use so-called 'Applicant-Installation Options' instead of paying them for much of the work.
(While they insist such an approach is only advantageous to developers who can't wait for their crews to install; I'm twice-shy & waiting for some outside estimates on that approach.)
But the kicker was added on at the very end. While 3ph 208/120Y would be a Special Facility; 3ph 240/120 would not. I can't recall the term I've seen used here, but this appears to be their delta service with one 240 err side center-tapped & grounded; 120V loads would come both directions off it alone. Yes, it's mentioned in their Green Book, at least in section 5-13.
My questions for the brain trust here..
1) Why would they *want* to offer that to us? It's just a different transformer secondary to them, right?
2) Can we stomach it?
Yes, all the 120 loads can be put on the one side; both halves.
We have one 3-ph 480 load [Don't ask...] already in place; I'd assume I can buy a 240:480 transformer as easily as a 208:480 one.
We could, I hope, buy 3ph motors rated for 208/240 or just 240.
But is it legal to run 240V single phase loads off the other two sides? That would mean they would be 120 & 360V above ground.
Or do we buy our own 240:208Y transformer? That makes sense from an initial purchase (to avoid the $pecial Facilitie$ standing) but at an efficiency cost.
We'd really like 3ph 208/120 wye; for a welder & a number of pumps: deep well, swimming pool/slides, and fire protection. The rub is, the house is 750 ft back crow-fly from the 3ph-221.5 kv pole line & PG&E wants a 1400 ft long route. PG&E has guesstimated $60k for that, and quoted us only (!!!) $29K for split phase 320A 240/120.
I gather that a large part of the $60K is that 3-ph is considered 'Special Facilities' & such is heavily marked up under Rule 2. [This is part of the muddle; I was told by Engineering that a 7.5+ HP motor would take us out of Special Facilities, but the lower level people disagree.]
However, we recently found out several details they had, well... I'll just say 'overlooked' telling us, and as a result we had a meeting with them. Now it seems we can use so-called 'Applicant-Installation Options' instead of paying them for much of the work.
(While they insist such an approach is only advantageous to developers who can't wait for their crews to install; I'm twice-shy & waiting for some outside estimates on that approach.)
But the kicker was added on at the very end. While 3ph 208/120Y would be a Special Facility; 3ph 240/120 would not. I can't recall the term I've seen used here, but this appears to be their delta service with one 240 err side center-tapped & grounded; 120V loads would come both directions off it alone. Yes, it's mentioned in their Green Book, at least in section 5-13.
My questions for the brain trust here..
1) Why would they *want* to offer that to us? It's just a different transformer secondary to them, right?
2) Can we stomach it?
Yes, all the 120 loads can be put on the one side; both halves.
We have one 3-ph 480 load [Don't ask...] already in place; I'd assume I can buy a 240:480 transformer as easily as a 208:480 one.
We could, I hope, buy 3ph motors rated for 208/240 or just 240.
But is it legal to run 240V single phase loads off the other two sides? That would mean they would be 120 & 360V above ground.
Or do we buy our own 240:208Y transformer? That makes sense from an initial purchase (to avoid the $pecial Facilitie$ standing) but at an efficiency cost.