A recent thread points out that the rules for generators that do not have factory installed OCPD are not completely clear. I am thinking of submitting the following:
Conductors shall be permitted to be tapped, without overcurrent protection at the tap, to a feeder as specified in 240.21(B)(1) through (B)(5). The tap shall be permitted at any point on the load side of the feeder overcurrent protective device. Section 240.4(B) shall not be permitted for tap conductors. Where the tap conductor originates at the terminals of a generator, the full load current of the generator shall be used as the rating of the line side overcurrent protective device for the application of 240.21(B).
Conductors shall be permitted to be tapped, without overcurrent protection at the tap, to a feeder as specified in 240.21(B)(1) through (B)(5). The tap shall be permitted at any point on the load side of the feeder overcurrent protective device. Section 240.4(B) shall not be permitted for tap conductors. Where the tap conductor originates at the terminals of a generator, the full load current of the generator shall be used as the rating of the line side overcurrent protective device for the application of 240.21(B).