240.21(B) and generators

Status
Not open for further replies.

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The language in 445.13(B) is poorly written. It clearly requires a listed overcurrent protective device, but also permits a CT and over current relay without requiring that combination of devices to be listed. Not sure that the controller would qualify as overcurrent relay.
I don't think you would ever find a listed combination of CT and a relay. There are probably more manufacturers of relays than there are of CTs.

But I can see you point of having the relay listed to provide over current protection equal to a listed OCPD. I know I was often creative in creating Time Current Curves for some generator protection.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I don't think you would ever find a listed combination of CT and a relay. There are probably more manufacturers of relays than there are of CTs.

But I can see you point of having the relay listed to provide over current protection equal to a listed OCPD. I know I was often creative in creating Time Current Curves for some generator protection.
I was thinking more in terms of the protective relaying used on higher voltage systems.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I was thinking more in terms of the protective relaying used on higher voltage systems.
I don't think I ever checked for a recognized label, they are usually components in bigger equipment.

Wouldn't the generator overcurrent protection be part of its controller listing?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I don't think I ever checked for a recognized label, they are usually components in bigger equipment.

Wouldn't the generator overcurrent protection be part of its controller listing?
There is a UL Guide information sheet for the protective relays, "Protective Relays (NRGU)".

No idea if that would be part of the controller listing for a generator..
 