Thanks for all the replies, guys.
Assume 75 degree terminations for this. Ed, you're right, the 60 degree column for 14 has dropped to 15A.
I saw this in a graphic from Mike Holt, and it threw me. In the 2005, 210.4(D) changed to begin including this scenario under the small conductor rule, since before that you could serve multioutlet loads that could be overloaded if you added a transformer to the mix.
I don't think the graphic is right, I don't think you get around 240.4(D) by adding a transformer, but I'm not entirely sure sitting here not looking at the NEC right this second.
Keep em comin'...