- Location
- Lockport, IL
- Occupation
- Semi-Retired Electrical Engineer
This is a existing installation, in proximity to the equipment I am working with, but not within my scope of work. A 480 to 120/208 transformer feeds an MLO panelboard less than 10 feet away. There are 5 breakers installed, but there is nothing to prevent installing more breakers. I was planning to notify the owner that this is a code violation. Now I am not so sure. I don't see anything in 240.21(C)(2) that requires a main breaker or that limits the protection of the secondary conductors to six breakers. I see the six breaker limit in 450.3(B) for protection of the secondary windings. So that would have to be the basis for a violation, if there is one. But I don't see a rule saying that the panel must not be capable of having more than 6 breakers installed, though I have heard of jurisdictions that enforce that interpretation.
Do I need to inform the owner of an issue, or can I let this sleeping dog lie?
Do I need to inform the owner of an issue, or can I let this sleeping dog lie?