Even if it was permissible to tap 4/0 to a 4/0 to feed multiple disconnects, it does not seem practicable.
Feeding a power panelboard (without a main) is not permitted because of 408.36(D) unless it was a Delta-Delta XFMR, but 240.21(C)(1) allows that anyway.
I suppose you could use it to feed a switchboard without a main as long as the OCPD add up to equal to or less than the conductor ampacity and rated secondary amps.
A lot of Code requirements are written to allow someones idea of good installation to be allowed, but I can't imagine what it would be in this case, except for the switchboard scenario.
Anyone have another take on this? What am I missing?