 - Chapel Hill, NC
 - Retired Electrical Contractor
What breaker size then?
I don't believe you can go up to the next size breaker so you have to use a 50 amp
If the primary OCPD is greater than 400A, then the max secondary OCPD is 175A.
If the primary OCPD is 400A or smaller, then there is no max size on the secondary OCPD.
I guess I don't get this at all
It's Table 450.3(B)
But we also have to comply with 240.21(C)?
400A primary OCPD
175A secondary OCPD
Are we saying that a #6 is still good? Not how I see it
#6 is the minimum allowable conductor size under 240.21(C)(6)(1) for this installation.
#2/0 is the minimum allowable conductor size under 240.21(C)(6)(2) for the 175A secondary c/b.
#2/0 is larger than #6, so #2/0 complies.
I guess I'm I'm a little confused on the OP. I thought he wanted to know the minimum secondary ampacity he could use.
Thats what I wanted to know. I have 2/0 feeding a 175A main breaker PNL.
That wasn't mentioned until recently.OK, I get it. Missed the part that said you had 2/0 and a 175 breaker. I thought we were looking for the absolute minimum regardless of load. All good I get it.