I'm a little confused regarding protection of transformer secondary conductors. Case in point:
I have a 75kva transformer with a 480v primary and a 208/120v secondary. I've got a 125A breaker feeding the primary with #2's and 1/0's coming off the secondary feeding a 150A load. The load is a machine with a factory installed fused disconnect. The secondary is roughly 75' in length. Am I correct in assuming this is a compliant installation or do I need to protect the secondary conductors right at the exit point of the transformer?
I have a 75kva transformer with a 480v primary and a 208/120v secondary. I've got a 125A breaker feeding the primary with #2's and 1/0's coming off the secondary feeding a 150A load. The load is a machine with a factory installed fused disconnect. The secondary is roughly 75' in length. Am I correct in assuming this is a compliant installation or do I need to protect the secondary conductors right at the exit point of the transformer?