Had someone come in and give us half the information about adding a demising wall to spit one suite into two.
Come to find out that there is only one panel and it is in one of the suites. I cited 240.24(B) as the violation.
Got a call this morning and they asked if they had to install a seperate meter of if the could just add another subpanel off of the one that already exists. I think just putting a breaker in the existing panel to feed a new one would still be in violation of the code section above.
I'm wondering if they could just put in double lugs in the one panel and feed the other. Only problem with that is, turn off the main to work on one panel, you would turn them both off.
Opinions?