kwired
Electron manager
- NE Nebraska
- EC
I am also confused about same scenario , I Have Load of 600 Amp (Load is Chiller Units , and at Nameplate it is mentioned that OCPD should be 800Amp) , The ampacity of Cable is 882 amp , but once i apply the de-rating factor the ampacity is reduced to 740 amp. Can i use 800 amp CB and is it accepted as per codes. If yes, please mention the Code reference.
What is MCA of the unit?
Lets assume it is 600 amps, and the nameplate ocpd is 800, then you have 740 amps of conductor (derating is proper, thing your actual ampacity is what is left afterward) which is greater than the required 600.
Next size up OCPD rule in 240.4(C) doesn't apply to art 430 and 440 applications.
If you use nameplate 600 amp or greater for conductors and 800 amps for OCPD you are compliant.
You may or may not have other details that could change the response, this assuming 600 is the MCA and 800 is the actual max OCPD stated on nameplate.