Article 240.4(B) appears to permit the use of an overcurrent device rated higher than the rated ampacity of the conductor as long as the listed conditions are met. For simplicity sake, I'm trying to determine if the NEC permits conductors properly derated to somewhere above 25 amps and somewhere below 30 amps to be used for an individual branch circuit supplying a single L6-30R receptacle. The installer has pulled eight current carrying conductors with temperature ratings higher (90C) than specified for terminations (60C) for ampacity adjustments and corrections (110.14(C)). The overcurrent protection device is a 30 amp molded case circuit breaker (non-adjustable).
Second part, doesn't this make the wire a fuse?
Any thoughts are appreciated.
Article 240.4(B) appears to permit the use of an overcurrent device rated higher than the rated ampacity of the conductor as long as the listed conditions are met. For simplicity sake, I'm trying to determine if the NEC permits conductors properly derated to somewhere above 25 amps and somewhere below 30 amps to be used for an individual branch circuit supplying a single L6-30R receptacle. The installer has pulled eight current carrying conductors with temperature ratings higher (90C) than specified for terminations (60C) for ampacity adjustments and corrections (110.14(C)). The overcurrent protection device is a 30 amp molded case circuit breaker (non-adjustable).