gsrandy
Member
- Location
- Sanford, Florida
The AHU in my area is interpreting NEC 240.40 defferently than I where we have a fuses at 277 volt 20 amp taping off a 60 amp riser circuit. The fuse holder is designed in a box with tamper proof screws attaching the cover plate. This I feel makes this accessible by only qualified personnel. The fuse will be able to be disconnected and locked off for service if required by the breaker serving the riser.This is an FCU riser on a large commercial project. They are currently requesting a local disconnect for each fuse. What is the opinion of the forum?