machodelmonte
- Port-au-Prince, Haiti
Hi all, thanks in advance for any help!
I'm running a microgrid in rural Haiti with approximately 850 metered customers connected to a diesel microgrid. I am in the process of upgrading the grid from it's current service, which is lines of 120/240 triplex distribution running through town and to the customers. Our lines got so long that we had lots of voltage drop at the ends of the lines. So we're now in the process of installing a 13.2/22.8kV medium voltage line with 120/240 split phase distribution across 4 transformers located throughout the town.
The new generators are 2 - Caterpiller 100kVA DE110 diesel units, connected with a double throw (i.e. only one can power the grid with one genset at a time, and switching requires a short power outage for our customers). We requested the generators be wired 277/480 wye. Then we plan to run that through our 3 - 75kVA step-up transformers to boost it to our 13.2/22.8kV 3-phase medium voltage, and then will drop the voltage down to the local 120/240 at each of the distribution transformers.
I know electrical basics but have limited knowledge of medium-voltage, so I worked with a local engineer to design and procure materials for the system. However, the transformers delivered to the site yesterday have me worried: they are rated for 240/480, rather than 277/480, although the step up voltage is correct at 13.2/22.8kV. Since we plan on connecting each line to the transformer, I feared that the 277 voltage would mean our line would be running at around 15.2/26.3kV or so, meaning our service would be higher than the 120/240 it was supposed to be.
I've attached the nameplate of the transformer.
Is there something I'm missing?! Hoping there is a way to make these work as we are in quite a remote part of Haiti; although we need to make sure we have the correct stuff.