No. Conductors are sized on the basis of the calculated load. You first determine the load, then you pick a conductor with at least that ampacity, then you pick an overcurrent device to protect the conductor. There is a set of standard ratings for overcurrent devices. It is in 240.6(A). The difference between the two articles you cited has to do with what you do when you have a conductor with an ampacity value that does not exactly match one of those standard ratings. If the ampacity is less than 800 amps, then you can use an overcurrent device that is the next higher standard rating. If the ampacity is higher than 800 amps, then you use an overcurrent device that is the next lower standard rating.