Typically a 601 will fit in an 800 amp frame as Bob said. This allows you to get very close to 600 amps of protection in an 800 amp frame.
 
Another member posted this info about a year ago, he works for a major fuse manufacturer.

laughing from reading the responses. A 601 fuse is designed to fit a Class L Switch/Disconnect, with a bolt-in pattern. These are usually installed in the "Mains". Every-once-in-awhile, I get a call out for a 401, 501, 601 amp fuse. As per UL 248, fuses are designed to hold 110% of their rating continuously. Some fuses are also rated to carry 500% for 10-20 seconds to ignore the motor inrush, however clear within 1/2 cycle (.008 seconds).

just my $.02
 
600A and smaller fuses are either blade or ferrule mounting. These blade and ferrules sizes are dictated by the ampacity of the fuse. There are fuse reducers available to allow a smaller 400A fuse to be mounted into a 600A "clip".

Above 600A reducers are not available. Historically a 601A fuse was used because per the standards a 600A fuse could not be a bolt-in style.

In just the past few years I have notice that the Class L fuse is now available with ampacities 600A and smaller, so the 601A is no longer needed.
 