AgreedI believe the issue of 'presumptive' loads/temps/ratings etc were part of the estimating process vs test taking process - the worst-case scenario took precedence in this case.
Sent from my SM-G935P using Tapatalk
If the vendor panel's supply is via a 30A breaker and #10 Cu it does not matter that the load side #10 is protected via a 32A breaker as it is protected by the 30A supply breaker.
In my "example" I am only considering Code compliance. If you want selective coordination then, by all means, replace the vendor panel breaker with one of a lower value. If you replace it with an NRTL listed standard 30A you will have to compare TCC's to determine which would trip first. If you replace it with an IEC 30A breaker, chances are the supply breaker will still trip first.That would stand to reason if we're considering overcurrent protection only. But what about short-circuit and coordination? I'm sure we'd want the 32A CB to trip before the 30A CB...in your example, you're basically saying the 32A doesn't exist.
If the unit is fed with a 30 amp breaker then it is compliant as the 30 amp device will protect the wire
It doesn;t matter because it is still protected by a 30 amp overcurrent protective device.Perhaps, but the cable on load side of the 32A CB is also rated 30A - don't think this is 'kosher'.
Changing the vendor supplied CB will require us to jump through too many hoops and red tape. I believe, in a perfect world we change out the 30A CB in the existing power panel and install a 40A CB and feed with #8Awg cable.