kwired
Electron manager
- NE Nebraska
- EC
Were each of those voltages available at same time? If so at what capacity of total kVA rating of the generator? It is easy to tap into windings to get different voltages, but you can only ground one point of the system. 120 volts single phase is achievable in multiple configurations from a typical 12 lead unit while providing other voltages and number of phases and is common, you are limited to capacity of the winding you are connected across less any capacity it is already supplying to other circuits. The base voltage of each winding is 120 volts. But to arrive with 208 or 277 volts you need a wye configuration or those values will just not be present, outside of the high leg only of a 240 volt delta connection, 120 volts is harder to achieve with 480/277 configuration though because voltage excitation needs boosted a little to get to 277 and will be about 138 volts across each winding.We recently had a vendor bring a demo unit for a process we use. We rented a diesel generator from a yard. I hooked it up, the demo unit need 480V at 30 amps. The generator had
pretty much everything available...120/220, 208 and 480 3P. Why not just do that? I don't know what it cost to rent the thing but for doing equipment demonstrations
it might be easier to just rent what you need at the site.
Some of those generators that have both 120 and 480 volt outputs on them very likely have separate sets of windings that are independent of one another to get these voltages.