Not sure what you are trying to say hereThe corner grounded transformer has zero voltage, thus it's known as the ghost or "fhantom"(sic) voltage transformer.
Methinks he meant the grounded conductor.Not sure what you are trying to say here
Fuses are not permitted in the grounded conductor of this system, or any other system, other than the rare case where they are being used as motor overload protection.The corner grounded transformer has zero voltage, thus it's known as the ghost or "fhantom"(sic) voltage transformer.
You still have 240 V between conductors. It's a delta transformer. 250.24(D)(3)
It looks just like a normal service. Some disconnects may not have a fuse in that ghost leg.
Could be a strip of copper in lieu of a fuse. They are rare and seldom used.
So use caution if you encounter a corner grounded transformer and think maybe the utility company lost one of their phases.
Thanks for reading.
Comments accepted.
TX+MASTER#4544
The code has always required the use of white or gray for that conductor, just like for any other grounded conductor. However, I have never seen white or gray used for this conductor in the field.Fun fact 240 corner grounded delta often used blue as the grounded phase, just like 416Y/240 systems use light blue as a neutral.
Blue never made it into the NEC as a permitted grounded conductor color other than flexible cords. Using blue as a neutral or grounded conductor requires 'special permission' from the AHJ.
Sure, but out at the street, the PoCo will use what they want - services sometimes come in colored as red/white/blue with a bare (or black!) neutral.The code has always required the use of white or gray for that conductor
I have tried to get our guys out of the old red, white, blue habit.Sure, but out at the street, the PoCo will use what they want - services sometimes come in colored as red/white/blue with a bare (or black!) neutral.
Yes, but the code starts at the service point and the grounded conductor on the load side of the service point must be identified in accordance with the rules found in Article 200. It does not make any difference that the utility used a different color on the line side of the service point.Sure, but out at the street, the PoCo will use what they want - services sometimes come in colored as red/white/blue with a bare (or black!) neutral.
Thats all I was pointing out that blue is typically the grounded conductor in a corner grounded.However, I have never seen white or gray used for this conductor in the field.
We have about a dozen on our entire system. Do not build new ones. We end up on too many trouble calls where someone is calling saying one leg is out when they put a voltmeter on it.Thats all I was pointing out that blue is typically the grounded conductor in a corner grounded.
I have never seen a corner grounded system supplied by a utility, only at a large facility that has a MV service and a whole list of systems.
Have never seen it as blue...most often just black like the other phase conductors and typically marked with phase tape, often black, red, blue.Thats all I was pointing out that blue is typically the grounded conductor in a corner grounded.
I have never seen a corner grounded system supplied by a utility, only at a large facility that has a MV service and a whole list of systems.
Thats weird they phase tape the grounded conductor black, red, blue?typically marked with phase tape, often black, red, blue.
sorry, I tried to say black, red, blue, one for each phase, the common low voltage phase conductors.Thats weird they phase tape the grounded conductor black, red, blue?
I would think it would just be blue phase tape.
I am just messing with you I think we were saying the same thing the grounded phase was usually marked blue in one way or another.sorry, I tried to say black, red, blue, one for each phase, the common low voltage phase conductors.