I'm with Trevor(Infinity) on this; there are inconsistencies in the original post, and these need to be resolved in order to help resolve Chris'(aelectricalman) questions.
The first is the '3 phase available' '3 phase not available' issue.
The second is the statement that A and C phases are brought to the panel with a neutral, and that B phase is jumpered to ground.
I believe the Pierre is making correct guesses given the above confusion; but until what the POCO is supplying is clarified, then they are guesses.
Chris: there is a system called corner grounded delta. The full 240V is available between all three conductors, and the system may be used to supply 3 phase loads. Loads may be connected between any of the legs; the grounded leg is a fully useable current carrying conductor. The only difference is that the leg is held at ground potential.
The grounded phase leg may be left without OCPD, or it may be protected by OCPD given the specific requirements for OCPD on a grounded conductor. Thus corner grounded delta may be fed to a three phase panel, and all breaker spaces used.
You may use a panel that looks like a single phase panel, with breakers only on the two ungrounded legs, and still feed 3 phase loads. The panel looks like a single phase panel, with two phase bus bars and a 'grounded conductor' bar, however there is a critical difference: the panel will be rated for the different voltages. Normal 240V single phase panels and breakers are rated for 240V leg to leg, but only 120V leg to ground. You would need a panel that was fully rated for 240V.
If you use a three phase panel, you also need to confirm that it is fully rated for 240V to ground, and not 'slash' rated 240/120V.
A serious inconsistency is that if you have a grounded phase leg, you _cannot_ also have a grounded neutral. But if you have a neutral in a 240V system, you are required to ground it. So the statement about bringing in A, C and Neutral , but then grounding B leg is quite confusing.
-Jon