dmplec said:Have you ever had a power company want a single phase meter base for a 3 phase delta 240 volt service with one leg not metered
dmplec said:allowing a splice in the meter will be difficult.
While we both know that is the code rule, have you actually seen that in the field? I have never seen a white used on this system as required by the code.iwire said:If I am right that it is corner grounded, that the grounded conductor will have to be marked white.
So a circuit to a 3 phase motor would have one white phase and two not white phases.
don_resqcapt19 said:While we both know that is the code rule, have you actually seen that in the field? I have never seen a white used on this system as required by the code.
raider1 said:I agree, all of the 240 volt corner ground delta systems that I have seen did not, in fact have the grounded conductor phased white.
Chris
don_resqcapt19 said:While we both know that is the code rule, have you actually seen that in the field? I have never seen a white used on this system as required by the code.
OK, and come back w/ the pictures of Main & Service Point. ...:roll:dmplec said:the service is not a corner grounded delta. it is a straight 240 volt 3 wire 3 phase delta service to run (2) 240 volt 3 phase machines and that is it.
You never have to meter all the legs, you need one less element (CT) than you have phases. Thanks Jimjim dungar said:Blondel's Theorem is at work.
With the restriction that the leg with the missing element is used as the common point for the voltage coils.charlie said:You never have to meter all the legs, you need one less element (CT) than you have phases. Thanks Jim![]()