gsurace said:One question about this system, I checked the voltage, phase to ground, on the leg which passed straight though and got 516V. Does this sound right? I did measure 230V phase-phase. I did not, for some reason, check the other two phases to ground.
In an ungrounded system is is possible for you to measure all sorts of weird voltages L-G. It all depends on the amount of coupling capacitance in the system and the impedance of your meter.
If you have a 240V nominal system you only need to use equipment that has been rated for use on a 240V ungrounded delta system.