I have a neutral.mdshunk said:Only if you want to.
120 volt eyes need a neutral.
domnic said:can i break one leg of a 240 volt lighting circuit with a 120 volt eye?
220/221 said:you have to break both legs on a manual switch
220/221 said:If you have to break both legs on a manual switch....
Who says you have to?
220/221 said:You can't use phase tape on #6 or smaller wire but you can leave half the circuit hot in a fixture?
220/221 said:I always assumed you had to.
Are you telling me that you can use a sp switch to control a 240V light?
(B) Switching Where supplied by the ungrounded conductors of a circuit, the switching device of auxiliary equipment shall simultaneously disconnect all conductors.
don_resqcapt19 said:What about 410.54(B)?
OK, I give up, what is a switched lampholder?:-?RB1 said:OK what about 410.48?
True, but they could be.No one has said that the lights in question where HIDs.
There are several varieties, but the one they're likely talking about in that code section are the switched mogul based lampholders for 240V lamps. Pretty much a bygone item.electricman2 said:OK, I give up, what is a switched lampholder?:-?
don_resqcapt19 said:Bob,
True, but they could be.
Don