240 Volt Only Circuit Breakers

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician (retired)
I saw this on another forum. Anyone want to take a crack at what the note on the bottom of the label means? Sound like slash rated circuit breakers are not permitted but that makes little sense. This panel is supposedly from the 60's.

GE.JPG
 
It says for a 2wire supply, 240V to ground, you cannot use slash rated breakers.

These types of manufacturer instructions were ignored for decades, until equivalent language was added to the NEC.
 
I think the phrase "additional rating" is the key to understanding this note. To me, it says that if you use a two-pole breaker for a circuit that needs no neutral, then the breaker you choose must be rated for 240 volts. That "additional rating" is in addition to the breaker rating of 120V required for single pole circuits.
 
It says for a 2wire supply, 240V to ground, you cannot use slash rated breakers.

These types of manufacturer instructions were ignored for decades, until equivalent language was added to the NEC.
I agree but I'm trying to think of a scenario where you would actually use that type of system to supply a panel. Two ungrounded legs of a corner grounded Delta?
 