• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

240 x 480-120/240 V Transformer Ratio

Merry Christmas
Status
Not open for further replies.

FaradayFF

Senior Member
Location
California
Greetings, Gents -
I'm a little confused on '240x480' designation on the high side of the transformer. This is different from ' 480-120/240' designation.
Does this mean that I can connect either 240V or 480V supply on the primary and get 240V/120V on the secondary side? What does "X' mean in this context?
The nameplate shows a SERIES and Parallel connections. I intend to utilize the series connection. This is a single phase transfomrer.
I intend to energize from 480V on the primary to obtain 240/120V on the secondary for my loads.

Thanks,
EE
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
There should be a diagram that comes with the Transformer that shows you how to hook up the primary side to either 240 or 480. Usually you jumper two of the windings in parallel for 240 and put them in series for 480.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The primary is made two 240v windings that can be wired in series or parallel, and the secondary is made of two 120v windings that also can be wired in series or parallel. You can use them in any combination.
 
I agree with the above. This made me think of something I've been trying to find for a while. It was a document giving a detailed explanation of all the transformer designations/symbols. Anyone know where that is? It would be good for the OP too.
 
I think what I am looking for is in this:
IEEE Std. C57.12.00

Hard to view, keep hitting pay walls.

Smart$ gave a link here post #26 but the link no longer works. Giving up for the night:

 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Greetings, Gents -
I'm a little confused on '240x480' designation on the high side of the transformer. This is different from ' 480-120/240' designation.
Does this mean that I can connect either 240V or 480V supply on the primary and get 240V/120V on the secondary side? What does "X' mean in this context?
The nameplate shows a SERIES and Parallel connections. I intend to utilize the series connection. This is a single phase transfomrer.
I intend to energize from 480V on the primary to obtain 240/120V on the secondary for my loads.

Thanks,
EE
B5A48626-C36F-49BE-B7F8-48DA62095579.png
 

Attachments

  • AB8FE28E-EE50-436A-842F-AD16706CE5B3.png
    AB8FE28E-EE50-436A-842F-AD16706CE5B3.png
    882.7 KB · Views: 53
Status
Not open for further replies.
Top