So would it be fair to say that the utility designation of 4160/2400 is just indicating that it can be used with either a single ended 2400 source or with a 4160Y/2400 source as long as in either case it is connected across a 2400V potential?
In the second case that would require an L-N connection to the wye source.
If the transformer has two insulated primary bushings, it could also be connected line to line IF the line to line voltage is 2400.
Not working for a POCO, I would agree.