system grounding
So would it be fair to say that the utility designation of 4160/2400 is just indicating that it can be used with either a single ended 2400 source or with a 4160Y/2400 source as long as in either case it is connected across a 2400V potential?
In the second case that would require an L-N connection to the wye source.
If the transformer has two insulated primary bushings, it could also be connected line to line IF the line to line voltage is 2400.
Not working for a POCO, I would agree.
Usually they will read, "4160gy/2400 or "4160grndy/2400" if it's a single bushing unit. Obviously you can use a two bushing unit connected L-N, but not a single bushing connected L-L (where L designates an ungrounded conductor). I would think these days a two bushing 2400 transformer is mostly extinct except for old units, as utilities have converted these systems to 4160y
That would be gy or grndy as in grounded wye, I assume.
The NEC designation 4160Y/2400 does not tell us one way or the other about whether it is a grounded system.
Remove the bonding strap connected to PRI X2 in the step up transformer. Connect it to SEC H2 along with the secondary grounded conductor (currently depicted as connected to enclosure on right side).
BTW, the secondary is simply a single voltage, assuming 4160V. It is definitely not 4160GY/2400, as this would be a 3Ø wye configuration.
I fully understand and agree with the "Remove the bonding strap connected to PRI X2 in the step up transformer".
However I do not understand: "Connect it to SEC H2 along with the secondary grounded conductor (currently depicted as connected to enclosure on right side)". I would not connect that PRI X2 to anything. Maybe you might be able to explain so I can understand.
I did not know he was using an oil-immersed transformer [with internal factory bondings] at the time I wrote that. Yea, de signs where dere but dey just flew right over me head. I was thinking dry transformer. Alas!
Remove the bonding strap completely and ignore all else in my earlier post.
I am still getting through all the responses. Sorry the email notifications quite coming in.
Essentially yes. If you put a meter between the neutral of the wye and the center point of the single phase transformer, you would measure a pretty stiff 138V. Connecting these two points would cause large circulating currents in the transformer(s), and if you ground these two points the current flow would depend on the ground electrode resistance.
My assumption is that the single phase transformer is most commonly used for step down operation, where the secondary is supposed to be grounded by the strap...but when this transformer is used for step up operation the strap needs to be removed.
-Jon
Yes most commonly used for step down. Can you explain how you came up with 138v please?
Robeward,
May I inquire into the application? Is this a step up because of a long wire run?
Exactly right. Long cable run. When we buy them we tell cooper when we are going to use it for step up operation but the strap seems to be installed regardless.
The trick is actually easier than it should be. You represent each voltage and phase by a vector that has length equal to the voltage and a direction equal to the phase angle.
To add two voltages (of arbitrary phase) together, you simply add the vectors (connect them head to tail).
It is rendered very easy since your transformer diagram already puts the coils in the appropriate directions.
Draw your symmetric 'wye' and call the length of each leg 277 'units'. The angle of each leg of the wye is the phase angle for that phase. The length between any two 'tips' of the wye will be 480 units, and its angle will be the phase angle of the 480V connection. Draw this 480V line, and find its midpoint. Measure the distance from the neutral of the wye to the midpoint of the 480V leg.
-Jon
seem to be a lot of discussion over the designation. couple things. you can't just rely on how many HV bushings you see for determining voltage. if you go back and look of the picture of the xfmr there are actually two HV bushings but they are internally tied. we use one for source and usually install an elbow MOV on the other.
i have an attachment provided by cooper that explains the designation. essentially the designation determines how the xfmr is built. either one coil/mid tap or two coils connected. internally grounded or not. some can be used in wye configurations and some can't. it references an ANSI standard that governs this but doesn't actually give the name. the file is too big. once i figure out a way to make it available i will post it.
-Jon
Dag. I was stuck in single phase mode. Forgot to take into account angles from the source. let me ponder on this.
document compressed and split. hope it helps explain things.
  • Pages from cooper single phase xfmr designation-ilovepdf-compressed part 1.pdf
  • Pages from cooper single phase xfmr designation-ilovepdf-compressed-part 2.pdf
Good article, thanks. Similar to the one Smart$ posted but this one is more specific for single phase and gives a little more detail with examples.
Yes the loop feed bushing can throw you off, it did the same to me. I have a step up step down setup serving my house, and I was also planning on using the loop feed bushing for an arrestor elbow.
Out of curiosity, did they supply a different transformer for the step up an down or are they both the same?
Yes technically there is a difference but without the order form showing which one is which, I don't think you could tell the difference just by looking at them. Physically there is not difference and I honestly don't know what would make them different. The impedance numbers are different but I am not sure it is enough to say they build them in a different way. Maybe someone up here could shed some light.