240V gfic breaker with no netural

Status
Not open for further replies.
Re: 240V gfic breaker with no netural

The line neutral is required for proper operation of the GFCI circuitry. The load neutral can be left open.
 
Re: 240V gfic breaker with no netural

I'd look at the instructions for the installation of the breaker. I've install 2 pole gfci breakers with out the load side neutral, however the line side neutral still had to be connected.
 
Status
Not open for further replies.
Top