S slh1944 Member Location North Carolina Aug 20, 2004 #1 can a 240v gfic breaker work with out a netural connected to the breaker, that is to protect the person not the equipment? :roll:
can a 240v gfic breaker work with out a netural connected to the breaker, that is to protect the person not the equipment? :roll:
C curt swartz Senior Member Location San Jose, CA Occupation Electrical Contractor Aug 20, 2004 #2 Re: 240V gfic breaker with no netural The line neutral is required for proper operation of the GFCI circuitry. The load neutral can be left open.
Re: 240V gfic breaker with no netural The line neutral is required for proper operation of the GFCI circuitry. The load neutral can be left open.
K ken987 Senior Member Aug 20, 2004 #3 Re: 240V gfic breaker with no netural I'd look at the instructions for the installation of the breaker. I've install 2 pole gfci breakers with out the load side neutral, however the line side neutral still had to be connected.
Re: 240V gfic breaker with no netural I'd look at the instructions for the installation of the breaker. I've install 2 pole gfci breakers with out the load side neutral, however the line side neutral still had to be connected.
S speedypetey Senior Member Location Hudson Valley, NY Aug 22, 2004 #4 Re: 240V gfic breaker with no netural Exactly. This is very typical in a pool filter.