I'm an engineer working on a technology demonstration project involving water heaters. It would be super beneficial if we could install a 240V outlet near the water heater on the existing water heater 240V 30A circuit. The dozen or so of these that we're doing are residential retrofits which will be signed off on by a PE, the city inspector, and performed by licensed electricians. I proposed removing the wire to the water, bringing it back to the wall in a junction box, installing an outlet in the box, and then installing a new length of 10AWG wire from the junction box to the water heater (not as a plug-and-cord, but hardwired). One electrician said it was against code (NEC 2014). I've looked a bunch and can't find what piece of the code it violates.
Is this against code? If so, which section? If not, is there any section I can reference to show that it is allowed?
I found the following in my search of the code for "water heater":
220.56 refers to kitchen equipment
220.82(B)(3)d refers to calculating the total dwelling load and proper service
220.83(A)(3)d refers to calculating the total dwelling load and proper service
220.83(B)(3)d refers to calculating the total dwelling load and proper service
220.84(C)(3)d refers to calculating the total dwelling load and proper service
230.23(B) excludes some water heaters from needing 8AWG overhead service conductors
230.31(B) excludes some water heaters from needing 8AWG underground service conductors
230.93 allows the locking of overcurrent devices to prevent tampering
422.11(F)(3) allows subdivision of circuits up to 120 amps
422.13 when calculating the load of an up-to-120gal water heater, it should be considered a continuous load
422.47 water heaters need temperature-limiting disconnects in addition to their thermostats (they are all manufactured that way) (exceptions for >180F, >60kW, or instantaneous-type water heaters)
550.12(D)(1) would prevent an outlet being installed on a water heater feed if the water heater was greater than 50% the circuit rating (18amp on 30amp is the most common, for instance) AND it was in a mobile home. It appears that it is within code to install an outlet on the same feed as a water heater, provided it is NOT a mobile home?
550.17(B)(2) excepts water heaters from continuity/operational/polarity tests
550.18(B)(4) refers to calculating total mobile home load and proper service
551.42(C) only two 120v thermostatically-controlled appliances can be install in an RV without energy management
552.46(A) only two 120v thermostatically-controlled appliances can be install in an RV without energy management
552.46(B)(3) refers to calculating total RV load and proper service
552.47(B)(4) refers to calculating total RV load and proper service
680.9 refers to electric pool water heaters680.26(B)(6)(b) refers to bonding/ground of electric pool water heaters > 50amps
Annex C has some example service calculations which include water heaters
Thank you very much for any and all help!
Is this against code? If so, which section? If not, is there any section I can reference to show that it is allowed?
I found the following in my search of the code for "water heater":
220.56 refers to kitchen equipment
220.82(B)(3)d refers to calculating the total dwelling load and proper service
220.83(A)(3)d refers to calculating the total dwelling load and proper service
220.83(B)(3)d refers to calculating the total dwelling load and proper service
220.84(C)(3)d refers to calculating the total dwelling load and proper service
230.23(B) excludes some water heaters from needing 8AWG overhead service conductors
230.31(B) excludes some water heaters from needing 8AWG underground service conductors
230.93 allows the locking of overcurrent devices to prevent tampering
422.11(F)(3) allows subdivision of circuits up to 120 amps
422.13 when calculating the load of an up-to-120gal water heater, it should be considered a continuous load
422.47 water heaters need temperature-limiting disconnects in addition to their thermostats (they are all manufactured that way) (exceptions for >180F, >60kW, or instantaneous-type water heaters)
550.12(D)(1) would prevent an outlet being installed on a water heater feed if the water heater was greater than 50% the circuit rating (18amp on 30amp is the most common, for instance) AND it was in a mobile home. It appears that it is within code to install an outlet on the same feed as a water heater, provided it is NOT a mobile home?
550.17(B)(2) excepts water heaters from continuity/operational/polarity tests
550.18(B)(4) refers to calculating total mobile home load and proper service
551.42(C) only two 120v thermostatically-controlled appliances can be install in an RV without energy management
552.46(A) only two 120v thermostatically-controlled appliances can be install in an RV without energy management
552.46(B)(3) refers to calculating total RV load and proper service
552.47(B)(4) refers to calculating total RV load and proper service
680.9 refers to electric pool water heaters680.26(B)(6)(b) refers to bonding/ground of electric pool water heaters > 50amps
Annex C has some example service calculations which include water heaters
Thank you very much for any and all help!