The simple answer to what is a neutral is found in the Code book.
Article 100 Neutral Conductor
Article 100 Neutral Point
Not very good answers, right?
A much better definition is found in 220.61(A) ".......neutral load shall be the maximum unbalance of the load....."
So, it takes 3 conductors to have a maximum unbalance load. Or 4 conductors from a Y system: 3 conductors and the neutral conductor.
Example using romex, a red and black and a white wire (12-3 WG). The white wire is a neutral conductor and meets the definition of needing 3 conductors to call it a neutral.
Example: If the red wire carries 15 amps and the black wire carries 11 amps, then the unbalance load is 4 amps, thus it is a neutral conductor.
A 12-2 WG (1white and 1 black wire) romex wire, the white wire is not a neutral, it is a white ground wire.
It returns current back to the source, so it is a current carrying conductor.
A common conductor is just what it says, it could be the switch leg of a 3 way switch or the hot for the switch (common).
You will find it on a small control transformer that may have different voltages to select from (not a door bell transformer)
My advice is to stop trying to label every thing a "common".
And think that you will need at least 3 wires to call it a neutral, 2 hot conductors and one white wire.
There's a formula for calculating the neutral current in a 4 wire circuit.
220.61(B) explains in detail if the neutral is permitted to be reduced in size or if there shall be no reduction of the neutral or grounded conductor.
Notice that a groundED conductor will normally be a neutral. (most cases)
A groundING conductor is not a neutral. An EGC is not a neutral nor a grounding electrode conductor. It is for bonding continuity.
Thanks for reading
Comments accepted
TX+MASTER#4544
The simple answer to what is a neutral is found in the Code book.
Article 100 Neutral Conductor
Article 100 Neutral Point
Not very good answers, right?
A much better definition is found in 220.61(A) ".......neutral load shall be the maximum unbalance of the load....."
So, it takes 3 conductors to have a maximum unbalance load. Or 4 conductors from a Y system: 3 conductors and the neutral conductor.
Example using romex, a red and black and a white wire (12-3 WG). The white wire is a neutral conductor and meets the definition of needing 3 conductors to call it a neutral.
Example: If the red wire carries 15 amps and the black wire carries 11 amps, then the unbalance load is 4 amps, thus it is a neutral conductor.
A 12-2 WG (1white and 1 black wire) romex wire, the white wire is not a neutral, it is a white ground wire.
It returns current back to the source, so it is a current carrying conductor.
A common conductor is just what it says, it could be the switch leg of a 3 way switch or the hot for the switch (common).
You will find it on a small control transformer that may have different voltages to select from (not a door bell transformer)
My advice is to stop trying to label every thing a "common".
And think that you will need at least 3 wires to call it a neutral, 2 hot conductors and one white wire.
There's a formula for calculating the neutral current in a 4 wire circuit.
220.61(B) explains in detail if the neutral is permitted to be reduced in size or if there shall be no reduction of the neutral or grounded conductor.
Notice that a groundED conductor will normally be a neutral. (most cases)
A groundING conductor is not a neutral. An EGC is not a neutral nor a grounding electrode conductor. It is for bonding continuity.
Thanks for reading
Comments accepted