Hi - Does this seem to be correct for a 240 volt arc welder. This welder is going to be used in a residential garage. It has a primary current of 50A and a 20% duty cycle. I used a 30A breaker and 10-3 Romex to feed a 30A receptacle. The welder already had a 30A plug - looks like it had been replaced at some point and I'm not sure what it originally had. The owner complained of the breaker tripping after 10 minutes or so of use. If my calculaions are correct I should be able to replace the breaker with a 50A.
My calculations - 30A x .45(20% duty cycle multiplier NEC section 630.1(A)
= 22.5A - the reason I chose #10 wire per table 310.16 and according to NEC section 630.12(A) overcurrent protection shall not exceed 200% of the primary current rating of the welder, wich made me decide a 50A breaker should be safe. Does this seem accurate?
My calculations - 30A x .45(20% duty cycle multiplier NEC section 630.1(A)
= 22.5A - the reason I chose #10 wire per table 310.16 and according to NEC section 630.12(A) overcurrent protection shall not exceed 200% of the primary current rating of the welder, wich made me decide a 50A breaker should be safe. Does this seem accurate?