240VAC Appliance User
New member
- Location
- Kuwait
This may be a very dated request, but I've failed to post it on the forum quite some time back.
January, 2011 EC&M's CODE BASICS paragraph on voltage limitations sparked a question.
For those of us who spend a fair amount of time living overseas, we accumulate various electrical devices which operate on nominal 240VAC, the typical standard in much of the world outside the USA.
My first read of 210.6 (A)(2) and the notes indicates it is not code complaint to have outlets for the use of cord connected appliance of less than 1440 VA, if there is more than 120VAC between the conductors supplying the terminals.
Moving over to 210.6 (C) (6), we find it is code allowable to have circuits with up to 277 VAC between conductors for cord-and plug connected utilization equipment.
This section has no power rating limitation, and using the broad definition of utilization equipment, it would seem
210.6(C)(6) is the way to allow the installation of 240VAC outlets in a residence to use 240VAC appliances and devices.
If this is the case, why is there these two seemingly conflicting sections of the NEC?
Also, if 210.6(C)(6) does not allow for 240VAC outlets for the use of 240VAC cord-and-plug devices, wouldn't it be safer to allow the use of 240VAC outlets for this purpose rather than to have portable step-up transformers used to power the 240VAC devices?
What would be the best way for a stateside application to use typical 240VAC corded appliances?
January, 2011 EC&M's CODE BASICS paragraph on voltage limitations sparked a question.
For those of us who spend a fair amount of time living overseas, we accumulate various electrical devices which operate on nominal 240VAC, the typical standard in much of the world outside the USA.
My first read of 210.6 (A)(2) and the notes indicates it is not code complaint to have outlets for the use of cord connected appliance of less than 1440 VA, if there is more than 120VAC between the conductors supplying the terminals.
Moving over to 210.6 (C) (6), we find it is code allowable to have circuits with up to 277 VAC between conductors for cord-and plug connected utilization equipment.
This section has no power rating limitation, and using the broad definition of utilization equipment, it would seem
210.6(C)(6) is the way to allow the installation of 240VAC outlets in a residence to use 240VAC appliances and devices.
If this is the case, why is there these two seemingly conflicting sections of the NEC?
Also, if 210.6(C)(6) does not allow for 240VAC outlets for the use of 240VAC cord-and-plug devices, wouldn't it be safer to allow the use of 240VAC outlets for this purpose rather than to have portable step-up transformers used to power the 240VAC devices?
What would be the best way for a stateside application to use typical 240VAC corded appliances?