LarrywdH
Member
- Location
- Menomonee Falls, WI, US
I have a system 480v 3ph to 240v 3ph delta to delta transformer which has a voltage detector device on the secondary, which is detecting voltage on the grounded enclosure, which has people walking by concerned, but the grounded cabinet is grounded back to another voltage source, not the 240v source because it is not grounded at the transformer.
The voltage between the grounded cabinet and the ground wire on the voltage detection device is 17volts, which is what is blinking the lights.
The voltage phase to ground is 130v on 2 phases, 158 on the 3rd. But since there is no path back to the source, I don't know what that really means.
I am told that it was installed that way on purpose, because grounding the circuit interfered with some testing of equipment.
I have another identical system which is not blinking the ground indicator lights, but I can't tell what the difference is.
I would prefer a grounded system, but that is not what I have.
Thanks for any insight.