Finally got back to take readings on this transformer, I don't always get to set my own priorities...
Voltage phase to phase:
X1-X2 240v
X1-X3 240v
X2-X3 240v
Voltage phase to ground,
Main Output breaker on;
X1 135v
X2 145v
X3 135v
Main Output breaker open/Leads to breaker disconnected attransformer
X1 146v
X2 132v
X3 132v
Ohms to Ground measured with 1000v Megger
X1 13G
X2 13.5G
X3 14G