question here…
Say you get load data per 220.87 and the peak demand is 18kW.
Wouldn't the 24kW be sufficient without load shedding?
just because its a 200 amp service doesn't mean it will ever see 200 amps.
The disconnect is rated for 200 amps.
If the calculated load or whatever method you use is 18kw then Imo the generator only has to be rated for that load so a 24kw would be compliant.
I do not have a code section on that