SSDriver
Senior Member
- Location
- California
- Occupation
- Electrician
I'm only talking about the controls in this post.
I know I get a lot of voltage spikes when I have larger Contactors open going back to the control circuit. Enough that 120v LED pilot lights flash when the contactors de-energize. I have tried surge suppressors, RC, and varistors mounted on the contactors that do help but not eliminate the issue. They help enough that the LED's don't burnout but you will get a smaller flicker.
I have a project that I will have a PLC, HMI, 3 pilot lights, and three 40A contactors. Space is very limited and I was wondering if I could use the same power supply for the contactors, pilot lights, PLC, and HMI. Everything that could run at the same time would be under 40va and I was looking at a 48va Power supply that would work for inrush and space wise as well. Will I run into issues? I was planning on putting some " IronHorse Surge Suppresser, varistor, RC "modules on each contactor. Only 2 would ever open at the same time. I don't use DC contactors that much and wasn't sure if the spike would be worse or better than on an AC circuit.
Thanks.
I know I get a lot of voltage spikes when I have larger Contactors open going back to the control circuit. Enough that 120v LED pilot lights flash when the contactors de-energize. I have tried surge suppressors, RC, and varistors mounted on the contactors that do help but not eliminate the issue. They help enough that the LED's don't burnout but you will get a smaller flicker.
I have a project that I will have a PLC, HMI, 3 pilot lights, and three 40A contactors. Space is very limited and I was wondering if I could use the same power supply for the contactors, pilot lights, PLC, and HMI. Everything that could run at the same time would be under 40va and I was looking at a 48va Power supply that would work for inrush and space wise as well. Will I run into issues? I was planning on putting some " IronHorse Surge Suppresser, varistor, RC "modules on each contactor. Only 2 would ever open at the same time. I don't use DC contactors that much and wasn't sure if the spike would be worse or better than on an AC circuit.
Thanks.