24VDC Control Circuit Intermittent Fault

Learn the NEC with Mike Holt now!
Status
Not open for further replies.

gar

Senior Member
Location
Ann Arbor, Michigan
Occupation
EE
220801-1720 EDT

beck693:

Anything new?

Reading back thru the posts I see many comments that make no sense.

For example, how can you expect a power supply to be the problem when the problem only occurs in a small portion of the total circuit? Many other circuit portions from that same power supply operate with no failure.

With very high probability the problem is in a small region of the total circuitry. Changing from a DC relay to an AC has no advantage. But using sealed contact reed relays would have a great benefit in a dirty environment.

.
 

TimWaldner

New User
Location
SD
Occupation
Electrician
I had the same problem in a coal fired boiler control panel. One of the VFD driven fans would just shut off for no apparent reason. The problem was the relays; just like gar said. They were 10 or 15 amp GP relays. I replaced all the control relays with (3A max) gold plated bifurcated contacts . Problem solved.
 