Hello everybody, glad to be back.
I have a 50 amp load that will be comprised of control voltages (digital inputs and digit outputs) and 50 amps may be a bit conservative it could be more like 30 amps. The problem is that the 24vdc source will be about 70 ft away. This blows up the cable sizing or does it? The instrumentation guy says there shouldn't be a problem with a #10 AWG. I'm not comfortable with that, either I size it at #2 or we provide a 24vdc converter at the load and bring the 110v the 70 ft. He doesn't want to do that because there are spacing issues at the load.
Am I off base?
I have a 50 amp load that will be comprised of control voltages (digital inputs and digit outputs) and 50 amps may be a bit conservative it could be more like 30 amps. The problem is that the 24vdc source will be about 70 ft away. This blows up the cable sizing or does it? The instrumentation guy says there shouldn't be a problem with a #10 AWG. I'm not comfortable with that, either I size it at #2 or we provide a 24vdc converter at the load and bring the 110v the 70 ft. He doesn't want to do that because there are spacing issues at the load.
Am I off base?