25 amp breaker????!

Status
Not open for further replies.

nift21

Member
what size wire runs off that??
I noticed one in a customers house, whats the story, never seen one before.

Whats the purpose, what size wire??
someone fill me in. =)

thanks in advance
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: 25 amp breaker????!

It could very well be a water heater with a 4500 w element. Or a motor load with 14 AWG conductor.
Or it what was on the truck.
 

tonyi

Senior Member
Re: 25 amp breaker????!

As well as the HVAC and H2O heater mentioned, there's many possible derating scenarios that could wind up with some wire having 25A ampacity.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 25 amp breaker????!

A 25 amp breaker does not necessarily need a 10 awg conductor.

HVAC equipment and motor loads come to mind.
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: 25 amp breaker????!

Hi Bob,

This comes to mind for me;
(D) Small Conductors. Unless specifically permitted in 240.4(E) through (G), the overcurrent protection shall not exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG, and 30 amperes for 10 AWG copper; or 15 amperes for 12 AWG and 25 amperes for 10 AWG aluminum and copper-clad aluminum after any correction factors for ambient temperature and number of conductors have been applied.
I didn't notice any exceptions........
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 25 amp breaker????!

Dave it is right there in 240.4(D)

(D) Small Conductors. Unless specifically permitted in 240.4(E) through (G), the overcurrent protection shall not exceed 15 amperes for 14 AWG, 20 amperes for 12 AWG, and 30 amperes for 10 AWG copper; or 15 amperes for 12 AWG and 25 amperes for 10 AWG aluminum and copper-clad aluminum after any correction factors for ambient temperature and number of conductors have been applied.
Take a look at table 240.4(G)

It is entirely code compliant to use a breakers in excess of the conductor ratings for motor loads and unit equipment.

Mike Holt has an example of 14 AWG on a 60 or 70 amp breaker feeding a motor load. :) :)
 

websparky

Senior Member
Location
Cleveland, Ohio
Re: 25 amp breaker????!

Hi Bob,

I'd like to see MH's example where the branch circuit conductors are allowed to be protected like that. Where can I find it?

Now, if you were talking about control conductors, then I could understand!
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 25 amp breaker????!

Dave I looked around for it, we get a Mike Holt code tip each week with our checks, I saw it on one of those.

We have to remember that a breaker for motor loads is not for overload but short circuit and ground fault protection only, motor and conductor protection is from the motor overloads.

Another time 240.4(D) gets passed aside is in the tap rules.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: 25 amp breaker????!

Dave,
A 1 hp 115 volt single phase motor has a full load current of 16 amps per Table 430.148. The motor branch circuit conductor must have an ampacity of 125% of the FLA per 430.22(A). 125% of 16 amps is 20 amps. A #14 TW has an ampacity of 20 amps per Table 310.16. 430.52 permits an inverse time breaker having a rating of 250% of the motor FLA to provide the branch circuit ground fault and short circuit protection. This would permit a 40 amp breaker to protect the #14 conductor.
Don
 

hurk27

Senior Member
Re: 25 amp breaker????!

Here's another way to look at it:
If you look at 240.5 (B) (1) it allows for a 18 AWG lamp cord to be used on a 20 amp circuit.
Of course this sounds excessive but there is two reasons why.
1. The Medium base socket in the lamp will limit the amount of current placed on the wire by the load. The same as the motor OVL's

2. If a short circuit were to occur in the lamp the resistance of this wire will still cause the OPCD to trip.

This is one reason I hesitate to install 20 amp circuits for general use receptacles. As I have seen some 20 awg tinsel cords on lamps from China that would not trip a 20 amp breaker. It would light up like a heating element.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 25 amp breaker????!

Originally posted by jimwalker:
I took mikes course about 8 years ago. I remember something about #14 being protected at a very high #
No i would never do it
Jim why not, the conductors are protected by the motor overloads?

You can not overload the 14s without the overloads tripping.

This is the same way we protect tap conductors, the overcurrent device is downstream from the conductors it protects.

If the wires short circuit or ground fault the 14s are more than enough to trip the breaker, in the same way we do not run full size ground conductors for circuits above 30 amps.
 
A

a.wayne3@verizon.net

Guest
Re: 25 amp breaker????!

How about A/C compressors with a min ampacity of 15 amps. and a max breaker of 25 amps.You can still wire for min and fuse for max.(it`s legal as far as code) I personally would not wire it in 14 ga. but it is allowed
 

nift21

Member
Re: 25 amp breaker????!

speedypetey it is a modular. very suprising that a 14awg wire would be allowed on a higher breaker than 15, it seems like a sin, lol
 
A

a.wayne3@verizon.net

Guest
Re: 25 amp breaker????!

It does seem like a sin but it`s not as long as the min ampacity is met(would I do it no)but it is allowed
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: 25 amp breaker????!

REmebmer for most applications the ampacity of 12 AWG THHN is 30. Only 240.4(D) limits it to 20 amperers after derating. Using a 14 THHN on a 50 Amp CB may not agree with you, but its OK per the code for a motor application.
 