My project requires a plug strip to serve cord-and-plug connected equipment (fans, laser printer, computer, monitor). By actual current measurement, the initial connected load is 12.8 amperes, so a 20A breaker with 12 AWG wire is being installed. Next year, a paper shredder (7A load) will be added to this circuit. This is too close to the 20A circuit rating, so it seems the circuit should be 25A with 10 AWG wire. However, the electrician says when the new load is added, all he has to do is replace the 20A breaker with a 25A breaker and leave the 12 AWG installed. Does this not violate NEC 240.4(D)(5)?