The real desire for grounding is to get a low enough resistance to trip a breaker during a ground fault. .
!!This statement is incorrect. The purpose of grounding is given in 250.4(A)(1)!!
At 25 ohms resistance, a ground rod will have 4 amps at 120 volts, in a fault where the earth is used as the return path to trip a breaker.
What I tell electricians in my classes is your number one job is bonding, which is creating the electrically conductive path to clear a fault. In a line to case fault, electrons go back to the source, not earth.
Unless you are dealing with a telecom site, dispatch center, etc, the resistance of the ground rods does not matter. Use a ufer ground, you get a low resistance at virtually no cost, If you need ground rods, drive two and go home.