Here is something to think about. Following is a proposal I submitted to change 250.58 of the NEC. While it may not appear to have anything to do with this discussion, please notice the very last statement made by the CMP for which I have made BOLD:
5-176 Log #386 NEC-P05 Final Action: Reject
(250.58)
____________________________________________________________
Submitter: Bryan P. Holland, Holland Electric
Recommendation: Add new text as follows:
Where separate services, feeders, or branch circuits supply a building and are
required to be connected to a grounding electrode(s), the same grounding
electrode(s) shall be used and the provisions of (1) are met:
(1) An approved audible or visible alarm shall be installed at each service to
indicate the grounded conductor brought to the service has opened.
Exception No. 1: In industrial installations, with written safety procedures,
where conditions of maintenance and supervision ensure that only qualified
persons service the equipment.
Exception No. 2: Where electric service and electrical maintenance are
provided by the building management and where these are under continuous
building management supervision.
Substantiation: Upon the opening of the grounded (neutral) conductor at one
service, potentially dangerous current will flow between the common
electrodes to both services. Any person who comes in contact with exposed
metal parts at the service equipment or grounding electrode system could be
exposed to lethal current.
Panel Meeting Action: Reject
Panel Statement: The submitter has not provided any technical substantiation
to require monitoring grounding electrode and grounding electrode conductor
integrity by audible and visible alarms. The Code is not structured to protect against abnormal conditions such as open neutrals that may develop.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
____________________________________________________________
So let's go all the way back to the very first post that started this discussion before open neutrals and Iraq got involved.
Here's what I know:
1. The Chair of CMP 5 - Ronald Toomer cannot explain why 25-ohms is significant.
2. The Chair of the TCC - James Carpenter cannot explain why 25-ohms is significant.
3. Nor has Mark Earley of the NFPA.
4. Nor has Mark Ode of UL.
5. Nor has John Minick of NEMA.
6. Nor has Maichael Johnston of NECA.
7. Nor has Mitchell Guthrie - TC Chair of the NFPA 780.
8. Nor has Donald Zipse of IEEE.
AND, I have failed to mention at least a dozen more EXPERTS. These are individuals I have had one on one conversations with on this topic and this topic alone.
(PS - Let's not get into a conversation about my proposal. I am not good with rejection and I would have prefered it was never brought up. Please keep to the topic at hand.)