hi all,
I am creating a preliminary design, I'm not a PE yet, here is the thought process:
tapping into a 2400A 480V gear for a 300kVA stepdown Delta-Y transformer(located outdoor ~ 150' from the gear), the load on the transformer is about 234kVA.
with the 25' tap rule i need my tap conductors t o be 1/3 of the feeder conductors which is 800A, I'm looking to install a disconnect within 25' and then run my wires to the transfomer.
Transformer Primary is 361A or 451A continuous; since my tap conductors have to be 800A rated or more can my disconnect still be 400A or do I now have to get an 800A disconnect because of the tap conductors? how about the wires from the disconnect to the transformer, can I reduce the wire size to an appropriate size for the 451A continous primary transformer? I understand being able to go up to 250% on the primary but I dont wish to do that given my load.
thank you,
I am creating a preliminary design, I'm not a PE yet, here is the thought process:
tapping into a 2400A 480V gear for a 300kVA stepdown Delta-Y transformer(located outdoor ~ 150' from the gear), the load on the transformer is about 234kVA.
with the 25' tap rule i need my tap conductors t o be 1/3 of the feeder conductors which is 800A, I'm looking to install a disconnect within 25' and then run my wires to the transfomer.
Transformer Primary is 361A or 451A continuous; since my tap conductors have to be 800A rated or more can my disconnect still be 400A or do I now have to get an 800A disconnect because of the tap conductors? how about the wires from the disconnect to the transformer, can I reduce the wire size to an appropriate size for the 451A continous primary transformer? I understand being able to go up to 250% on the primary but I dont wish to do that given my load.
thank you,