250.119 allows the equipment ground in a multi conductor cable to be re identified. It seems to specifically allow this in NM cable. What is the need for this change?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
250.119 allows the equipment ground in a multi conductor cable to be re identified. It seems to specifically allow this in NM cable. What is the need for this change?
Which part of 250.119 allows an EGC to be re-identified when using NM cable? 250.119(B) allows another conductor to uses as an EGC. You can use a 3-wire NM or MC cable for something like an isolated grounded circuit where you need two EGC's. The red conductor is taped green and used as the IG.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You can use a 3-wire NM or MC cable for something like an isolated grounded circuit where you need two EGC's. The red conductor is taped green and used as the IG.
With MC, I use the green conductor as the IG and strip all the red to use as the EGC.
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
Aside: what code section(s) specifies which conductors have to be insulated, as opposed to just covered?

For example, suppose I need to run 4 ungrounded conductors (including switched conductors), a grounded conductor, and an EGC between two non-metallic boxes on a 15A branch circuit using NM cable. Is it permitted to run (2) 14/2 NM cables, using one bare conductor as the EGC, one bare conductor as the grounded conductor (which would everywhere be either covered by the NM jacket or field insulated with white insulation/tape), and the four insulated conductors as the 4 ungrounded conductors? We could route the two cables one on top of each other to avoid creating a current loop and associated EMI.

Obviously that doesn't seem right, but am looking for the exact code citations. In particular if there's a section which says the grounded conductor for a branch circuit has to be insulated.

Thanks,
Wayne
 

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
250.119 allows the equipment ground in a multi conductor cable to be re identified. It seems to specifically allow this in NM cable. What is the need for this change?
I raised this issue after taking a code update online program. This update was covered and it was mentioned that this was intened to apply to NM cable. I asked because I did not understand the need for this change to the code.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I raised this issue after taking a code update online program. This update was covered and it was mentioned that this was intened to apply to NM cable. I asked because I did not understand the need for this change to the code.
What code cycle had a significant change and what was the change? I don't see much difference over the last 4 code cycles.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Aside: what code section(s) specifies which conductors have to be insulated, as opposed to just covered?
310.3(D)
For example, suppose I need to run 4 ungrounded conductors (including switched conductors), a grounded conductor, and an EGC between two non-metallic boxes on a 15A branch circuit using NM cable. Is it permitted to run (2) 14/2 NM cables, using one bare conductor as the EGC, one bare conductor as the grounded conductor (which would everywhere be either covered by the NM jacket or field insulated with white insulation/tape), and the four insulated conductors as the 4 ungrounded conductors? We could route the two cables one on top of each other to avoid creating a current loop and associated EMI.

Obviously that doesn't seem right, but am looking for the exact code citations. In particular if there's a section which says the grounded conductor for a branch circuit has to be insulated.

Thanks,
Wayne
It would violate 300.3 and 310.3(D)
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Maybe applies to repurposing old NM cable with no ground to a grounded circuit with a taped green ground. But you would need to be converting a -3 cable to a -2 type usage which seems uncommon.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I raised this issue after taking a code update online program. This update was covered and it was mentioned that this was intened to apply to NM cable. I asked because I did not understand the need for this change to the code.
The only change since the 99 code was the removal of these words in the 2020 code.
Where the conditions of maintenance and supervision ensure that only qualified persons service the installation
The substantiation for this change was:
There is no logical reason why the requirement "Where the conditions of maintenance and supervision ensure that only qualified persons service the installation" exists for re-identifying conductors of a multi-conductor cable. No such requirement exists for reidentifying conductors sized 6 AWG or smaller in 200.6(A) or for conductors sized 4 AWG or larger in 200.6(B). No such requirement exists in 200.6(D) for reidentifying conductors of different systems that are installed in a raceway, cable, box, auxiliary gutter, or other type of enclosure. Section 210.7(C)(1), which covers the use of conductors in (multiconductor) cables with insulation that identifies them as grounded conductors, permits conductor insulations to be reidentified to indicate its use. Specific instructions are given for such reidentification. In addition, specific requirements are provided for use of reidentified conductors for switch loops. This reidentification of conductor insulation is permitted without a requirement for qualified persons in qualified occupancies. No such requirement exists in 210.5(C) for branch circuits for "Where the conditions of maintenance and supervision ensure that only qualified persons service the installation" only qualified persons perform these identification tasks. The identification of the grounded conductor in feeders simply refers back to 200.6 without additional requirement. Extensive requirements exist in 215.12 for identification of equipment grounding conductors and for ungrounded conductors. No requirement exists for such tasks to be performed by only qualified persons in qualifying facilities. General requirements for identification of conductors is found in 310.110. There is no requirement for identification "Where the conditions of maintenance and supervision ensure that only qualified persons service the installation" in Article 310. General requirements for identifying equipment grounding conductors are found in 250.119. As found in 250.119(A), re-identification of conductors 4 AWG or larger can be performed by anyone without restriction. Many other sections of the NEC permit or require identification. So far as this submitter can determine, there is no requirement similar to "Where the conditions of maintenance and supervision ensure that only qualified persons service the installation" to perform such identification. A companion public input intends to correct 200.6(E).
And the panel statement in accepting this change was:
The Panel edits the text. Many other sections of the NEC permit or require identification. There is no requirement similar to "Where the conditions of maintenance and supervision ensure that only qualified persons service the installation" to perform such identification.
There was no mention of NM in this change, and this change simply made this rule match similar rules in other code sections.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
For example, suppose I need to run 4 ungrounded conductors (including switched conductors), a grounded conductor, and an EGC between two non-metallic boxes on a 15A branch circuit using NM cable. Is it permitted to run (2) 14/2 NM cables,
This part about using two 14/2 cables in your example is the violation of 300.3 (B)
 