ok, i understand. Is there a code reference for that
I believe that would be 250.122(B).
ok, i understand. Is there a code reference for that
Say for the sake we're considering this an old installation, wouldn't you be violating the condition to have either SE cable or an insulated grounded conductor anyway?
Since you're essentially running a new circuit, and having a new installation for the dryer, wouldn't you need to have a 4 wire installation?
If I ran a new circuit agreed. If the BC was there and it is an old dryer brought in with lets say new home purchase? Just playing devils advocate (or NEC advocate as it may be), but Iwire probably is correct in his assumption of put the 40 Amp breaker in. The Handbook uses the (VD or any other reason) in the comments.
Not true, 250-57 required an EGC, article section 250-60 only allowed using the grounded conductor for ranges and dryers and only if certain conditions were met.Prior to the 1996 Code, use of the grounded circuit conductor as a grounding conductor was permitted for all installations.
I hate to say this but you are daisy chaining, violations as you go, installing a 40 amp breaker, to allow the #10 EGC in the 8/2 will now create the requirement, of a 40 amp dryer receptacle (don't think you will find one), the 40 amp dryer receptacle will require a 40 amp dryer cord, a 40 amp dryer cord will require a 40 amp dryer????
why not just install the proper 10/3 4-wire circuit and be done with it?:roll:
Roger,
The quote w/regards to the 99 code came from the NEC handbook. I'll defer to them...
I'm not specifically talking about going from the 30 -> 40, but having a circuit wired with 8-2 NM-B that is supposed to be a dryer circuit.
Yes, but if NM was used, the neutral had to be insulated. That's been required for decades.Agreed, but there were instances where NM was used.
Prior to the 1996 Code, use of the grounded circuit conductor as a grounding conductor was permitted for all installations.