chris kennedy
- Miami Fla.
- Retired electrician
I have a 150kva tranny, 208 Delta primary to 480y/277 secondary. From each ungrounded secondary bus I will have four #6's tapped to 4 AC disco's. The 208 primary is fed from a 400A breaker. Here is my confusion.
FWIW, this install will comply with 240.21(C)(4).
Thanks
So essential there is no OCPD ahead of the taps, (SDS), so would I base the EGC on the 400A primary OCPD??? I understand it doesn't have to be larger than the tap conductors in this case, just wondering.250.122(G) Feeder Taps.
Equipment grounding conductors run with feeder taps shall not be smaller than shown in Table 250.122 based on the rating of the overcurrent device ahead of the feeder but shall not be required to be larger than the tap conductors.
Thanks