My brother is electrical contractor in Colorado and I am an electrical contractor in Florida. From our conversations Colorado seems to “strain the gnat” on the NEC . For example, my brother recently failed an inspection after installing a new 200 amp outdoor disconnect (residential).
The indoor electrical panel was existing.
The range & dryer had an existing three wire system. Because he implemented a new outdoor main disconnect which previously just had a meter can, the inspector now is obligating the homeowner to upgrade to a four wire system for the range and dryer. He said that if the range and the dryer went to the service equipment it would be permissible.
In 250.140 it allows a neutral to case connection .
In the 2020 handbook (commentary) it does talk about type SE cables supplying ranges that were required to originate at the service equipment to avoid neutral current from downstream panel boards being imposed on metal objects such as pipes and ducts. But nowhere in the code does it say that these 3-wire circuits have to originate at the service today.
If I have an indoor electrical panel that is fed with a four wire SER cable and The range circuit is fed with a three wire branch circuit with a neutral to case bond ..,that should be permissible? Correct? Why would the 3-wire rang circuit have to go all the way back to the service equipment?
Why would this Colorado Inspector obligate the electrician to upgrade to a four wire system when all he was doing was installing a new outdoor disconnect?
The indoor electrical panel was existing.
The range & dryer had an existing three wire system. Because he implemented a new outdoor main disconnect which previously just had a meter can, the inspector now is obligating the homeowner to upgrade to a four wire system for the range and dryer. He said that if the range and the dryer went to the service equipment it would be permissible.
In 250.140 it allows a neutral to case connection .
In the 2020 handbook (commentary) it does talk about type SE cables supplying ranges that were required to originate at the service equipment to avoid neutral current from downstream panel boards being imposed on metal objects such as pipes and ducts. But nowhere in the code does it say that these 3-wire circuits have to originate at the service today.
If I have an indoor electrical panel that is fed with a four wire SER cable and The range circuit is fed with a three wire branch circuit with a neutral to case bond ..,that should be permissible? Correct? Why would the 3-wire rang circuit have to go all the way back to the service equipment?
Why would this Colorado Inspector obligate the electrician to upgrade to a four wire system when all he was doing was installing a new outdoor disconnect?