If that metallic box is isolated (as in has no metal raceway or other method of bonding it) it will need bonded to the EGC regardless if any other conductors are spliced within the box. Did not look it up but pretty sure this is require to be bonded by a different section then the portion that allows us to pass through when no other splices are made.
How close are you looking for, I bet they are all in 250 and within the equipment grounding and/or bonding sectionsMaybe all it would take would be for the Different Sections to be a little closer for clarity.
JAP>
Sure, via the conduit.
Always try to intall the EGC on the inside of an LB so It'll dig in first....
JAP>
In my opinion the code generally prohibits using a metal LB in the middle of a non-metallic raceway run such as PVC. Maybe there would be a weird case where 250.86 Exception 1 would apply. 250.86 Exception 3 covers buried metal elbows but LBs are supposed to be accessible so they don't get to benefit from that. I can't really think of an approved way to bond a metal LB other than by using a bonded raceway on at least one side of it.
I agree that the rule on splicing in boxes doesn't make a lot of sense on the face of it. If the general idea is that bonding through metal raceways is not reliable enough, then the rule would make more sense if it required wire EGCs everywhere, or for raceway runs exceeding a certain length, or something like that. Not that I think such a rule would improve the code.
:slaphead:
I suspect we got here through a general notion that some redundancy is a good thing, and this is a relatively simple way for the code to build in some redundancy, without making a really complicated rule that might in the end be no less arbitrary.
Yea, but that makes completely too much sense.....
JAP>
Here is an illustration that will help and you are right, if there are no splices in the box the EGC can be the metallic conduit as ActionDave says.
Roger
If you read the general statement carefully, it requires "any equipment grounding conductor(s) associated with those circuit conductors shall be connected within the box or to the box". The circuit conduits are equipment grounding conductors? It is only subsection (C) that requires connection to a metal box. You have three choices for compliance with (C). I believe your example would comply as long as other equipment grounding conductors are also connected to that of your example. Note the box itself is not specifically called an equipment grounding conductor anywhere in the NEC....Suppose one of the metal raceways terminates with a bonding bushing and a standard locknut (no KOs remaining), which would establish continuity to the enclosure. Is it acceptable to land the EGC on the bonding bushing's lug, and still meet the intent of this rule?
But is part of the EGC path when there is no wire EGC pulled in the raceways.Note the box itself is not specifically called an equipment grounding conductor anywhere in the NEC.
But is part of the EGC path when there is no wire EGC pulled in the raceways.
Part of the equipment grounding path, but not part of the equipment grounding conductor... technically.But is part of the EGC path when there is no wire EGC pulled in the raceways.
Part of the equipment grounding path, but not part of the equipment grounding conductor... technically.
Question: If a wire-type EGC is pulled, is an EGC-qualifying metal conduit still an EGC?
In a very, very... very indirect manner, I suppose. :happyno::happyyes:First sentence is the answer to the question in the second sentence here.
Part of the equipment grounding path, but not part of the equipment grounding conductor... technically.
Question: If a wire-type EGC is pulled, is an EGC-qualifying metal conduit still an EGC?