gregRooster
- United States
Understanding 250.188(E)
Can anyone explain what the basis for 250.188(E) is?
Why would you not connect the grounding electrode of the portable system to the rest of the system? If you connect the portable device so that the equipment grounding conductor bonds to existing systems, then any lightning will find a path through the ECG from one electrode to the other. This seems totally counter to the rest of the code.
250.188(E) Isolation. The grounding electrode to which the portable or mobile equipment system neutral impedance is connected shall be isolated from and separated in the ground by at least 6.0 m (20 ft) from any other system or equipment grounding electrode, and there shall be no direct connection between the grounding electrodes, such as buried pipe and fence, and so forth.