From posting in another thread I find I have a question on interpreting 250.20(B) in regard to a SDS
(B) Alternating-Current Systems of 50 Volts to 1000Volts. Alternating-current systems of 50 volts to 1000 voltsthat supply premises wiring and premises wiring systemsshall be grounded under any of the following conditions:
(1) Where the system can be grounded so that the maximumvoltage to ground on the ungrounded conductorsdoes not exceed 150 volts
(2) Where the system is 3-phase, 4-wire, wye connected inwhich the neutral conductor is used as a circuit conductor
(3) Where the system is 3-phase, 4-wire, delta connected inwhich the midpoint of one phase winding is used as acircuit conductor
Would a 208/120 system with n XO terminal in which the neutral was not used as a circuit conductor be required to be grounded? (1) above would indicate "yes" but (2) above might lead one to say "no" unless (2) applies to system over 150 volts to ground.