250.21(A)(3) and 250.30(A)

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
I have a vendor drawing that shows a 2 wire 2000VA control transformer 480-240V, (H1 and H4 connected to X1 and X4 respectively).
It feeds a small heater on an overhead crane. The secondary side is NOT showing a grounded conductor or a GEC, but the system overall is grounded and the heater shows a connection to plant earth (PE). I’m thinking there needs to be a conductor connected to X2 on the XFMR ran to the heater. Thoughts?


Sent from my iPhone using Tapatalk
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
it’s a two winding control transformer


Sent from my iPhone using Tapatalk
But when you say (H1 and H4 connected to X1 and X4 respectively), that makes me think the two windings are wired like this, which would mean it is already grounded by the equipment ground. 1690904650293.png
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
IMO, it doesn't meet the criteria of 250.21(A)(3) but it also doesn't meet the requirements in 250.21(B).
Seemingly you would be fine but need to add a detector per 250.21(B)
 
Top